I guess its all on the edge for a 650VA UPS.
It's not 650VA UPS, but 390W UPS... Assuming honest specs.
Volt-amperes matter only with non-PFC load/in AC circuitry they don't measure actual real power, which is measured in watts.
Hence with modern PCs that VA number is completely meaningless and if UPS can provide enough watts, it can handle what little reactive power component there's present.
But because of VA number being bigger, marketroids like pushing those.
Usually "power factor" of UPS is 0.6, meaning real output power is 0.6 times VA number.
High end models usually have it higher, while in lower end UPSes it can be lower.
APC even has had some scam models with PF of 0.5 meaning their actual output power is half the advertising number.
You just need to skip that VA number completely and look for watts.
For better gaming PCs would set UPS requirement to 500W.
That also leaves some margin, because obviously it's not wise to size something for being red line loaded.
Also transfer to battery power might not be succesfull, if power draw is near full output of UPS.
Except for seamless power providing on-line/double conversion UPSes, there's short no voltage time before UPS kicks in, which no doubt causes higher momentary power draw to fill up PSU's bulk capacitor charge.
I'm not sure why but usually around 03:00AM the power just drops for a tiny second leaving TV and everything else off after that.
Do you have any big factories/industrial plants nearby?
Such very high power consumers can cause hiccups into local power grid when they turn things on/off.
Yep. Just a CB20 bench puts a 83% load onto the UPS. Including gaming thats pretty much close or even over the top on what it's capable of. It is changing the voltage a bit too tho.
That difference between input and output is no doubt far below measuring accuracy limit.
I mean when that whole UPS costs only fraction of higher end multimeters you can be sure there's some hefty tolerances in things.