i am gong by this house the most here is a 40 and its for the in this panel the 2 40 that are in it are base board heat and the stove is off a 20 the hot water tank 40 gal is off a30 this place is also 60 years old so i don't know if its up to codewrong, wrong, wrong, i spent 30 years working on, building, and repairing a/c heating and electrical things in houses:
dryer= 30 amp breaker
water heater= 30 amp breaker, 40 amp if its a 50 gallon
stove= 50 amp breaker
outdoor a/c unit= 30 amp for up to 3 tons, 40 amp for 3 1/2 to 4 tons, or 50 amp for 5 tons