Why would my UPS turn off while under minimal load?

MostlyCrazy

New Member
Joined
Dec 12, 2018
Messages
1 (0.00/day)
I have a Cyberpower UPS model BRG1500AVRLCD, 900 watts. Currently I have my desktop, monitor, and Router (TpLink AC3150, 60 watts) plugged into this. With my desktop, monitor and Router running my UPS has an estimated run time of 70 minutes. I have fiber based internet with it's own battery that lasts about 24 hours and doesn't require constant building power. Not too long ago we had a blackout that lasted several hours. My desktop and monitor were turned off and only the Router was running.

The router would run for about 20 minutes and then the UPS would shut down. The front screen said it had an estimated run time of 120 minutes, but would shut down after about 20. I could restart it and it would run fine for right at about 20-25 minutes again before shutting off. It seemed, although I didn't do actual testing, that if I was loading pages or streaming something it seemed to delay the shutdown. So it seemed like the UPS was shutting down when there was only a tiny power draw but not when it had an actual power load.

The Cyberpower web site doesn't mention anything and google only returns 20 pages of people asking why their UPS is beeping. I have the Powerpanel software installed and I don't see any settings that could effect this behavior. Any ideas why the UPS would shut off despite having plenty of power left and is there a way to stop this?
 
Joined
Mar 18, 2015
Messages
2,960 (0.90/day)
Location
Long Island
Check your sleep settings ... Im wondering if the UPS is **thinking** ... "well if he's not here, why should I be ? " :)
 
Joined
Aug 20, 2007
Messages
20,709 (3.41/day)
System Name Pioneer
Processor Ryzen R9 7950X
Motherboard GIGABYTE Aorus Elite X670 AX
Cooling Noctua NH-D15 + A whole lotta Sunon and Corsair Maglev blower fans...
Memory 64GB (4x 16GB) G.Skill Flare X5 @ DDR5-6000 CL30
Video Card(s) XFX RX 7900 XTX Speedster Merc 310
Storage 2x Crucial P5 Plus 2TB PCIe 4.0 NVMe SSDs
Display(s) 55" LG 55" B9 OLED 4K Display
Case Thermaltake Core X31
Audio Device(s) TOSLINK->Schiit Modi MB->Asgard 2 DAC Amp->AKG Pro K712 Headphones or HDMI->B9 OLED
Power Supply FSP Hydro Ti Pro 850W
Mouse Logitech G305 Lightspeed Wireless
Keyboard WASD Code v3 with Cherry Green keyswitches
Software Windows 11 Enterprise (legit), Gentoo Linux x64
It probably can't detect a load that low, and shuts down to attempt to preserve the battery.
 

Kursah

Super Moderator
Staff member
Joined
Oct 15, 2006
Messages
14,666 (2.30/day)
Location
Missoula, MT, USA
System Name Kursah's Gaming Rig 2018 (2022 Upgrade) - Ryzen+ Edition | Gaming Laptop (Lenovo Legion 5i Pro 2022)
Processor R7 5800X @ Stock | i7 12700H @ Stock
Motherboard Asus ROG Strix X370-F Gaming BIOS 6203| Legion 5i Pro NM-E231
Cooling Noctua NH-U14S Push-Pull + NT-H1 | Stock Cooling
Memory TEAMGROUP T-Force Vulcan Z 32GB (2x16) DDR4 4000 @ 3600 18-20-20-42 1.35v | 32GB DDR5 4800 (2x16)
Video Card(s) Palit GeForce RTX 4070 JetStream 12GB | CPU-based Intel Iris XE + RTX 3070 8GB 150W
Storage 4TB SP UD90 NVME, 960GB SATA SSD, 2TB HDD | 1TB Samsung OEM NVME SSD + 4TB Crucial P3 Plus NVME SSD
Display(s) Acer 28" 4K VG280K x2 | 16" 2560x1600 built-in
Case Corsair 600C - Stock Fans on Low | Stock Metal/Plastic
Audio Device(s) Aune T1 mk1 > AKG K553 Pro + JVC HA-RX 700 (Equalizer APO + PeaceUI) | Bluetooth Earbuds (BX29)
Power Supply EVGA 750G2 Modular + APC Back-UPS Pro 1500 | 300W OEM (heavy use) or Lenovo Legion C135W GAN (light)
Mouse Logitech G502 | Logitech M330
Keyboard HyperX Alloy Core RGB | Built in Keyboard (Lenovo laptop KB FTW)
Software Windows 11 Pro x64 | Windows 11 Home x64
I know my Cyberpower UPS has two options to set. Shut off after running for XX minutes and shut off with xx minutes remaining. It's a 1000PFCLCD from about 3 years ago iirc.

What are your settings in the CyberPower PowerPanel?

I'd suggest performing some more testing too, pull the power from the wall and do a rundown test with different loads (router only, router + PC + monitor, PC + monitor). Do they all exhibit the same results that you're reporting here?

I've seen more UPSes stay on in the event of a low load with no wall power rather than turn off, unless they were configured to do so or had a circuitry or battery cell issue. Those usually exhibit different symptoms as well. I suggest starting with verifying how PowerPanel is configured and load testing via software and manually.

How old is this unit? May still be under warranty. Says 5-year warranty here: https://www.cyberpowersystems.com/product/ups/brg1500avrlcd/
 

FordGT90Concept

"I go fast!1!11!1!"
Joined
Oct 13, 2008
Messages
26,259 (4.65/day)
Location
IA, USA
System Name BY-2021
Processor AMD Ryzen 7 5800X (65w eco profile)
Motherboard MSI B550 Gaming Plus
Cooling Scythe Mugen (rev 5)
Memory 2 x Kingston HyperX DDR4-3200 32 GiB
Video Card(s) AMD Radeon RX 7900 XT
Storage Samsung 980 Pro, Seagate Exos X20 TB 7200 RPM
Display(s) Nixeus NX-EDG274K (3840x2160@144 DP) + Samsung SyncMaster 906BW (1440x900@60 HDMI-DVI)
Case Coolermaster HAF 932 w/ USB 3.0 5.25" bay + USB 3.2 (A+C) 3.5" bay
Audio Device(s) Realtek ALC1150, Micca OriGen+
Power Supply Enermax Platimax 850w
Mouse Nixeus REVEL-X
Keyboard Tesoro Excalibur
Software Windows 10 Home 64-bit
Benchmark Scores Faster than the tortoise; slower than the hare.
1) Verify that everything is plugged in correctly. By that, I mean battery stuff in battery outlets and non-battery stuff into surge outlets.
2) Do you have CyberPower PowerPanel installed on the computer? If you do, it can be telling the UPS to go off after x minutes without power. By default, that's two minutes. Check its settings.
3) Most CyberPower UPSs have two separate circuits: battery which is controlled by the power switch and surge which is always on (uneffected by the power switch).
4) The time estimate is only accurate while there is no mains power and it is drawing on the battery. 20 minutes may be all the charge it's good for. Hard to say.
5) That particular UPS is a simulated square sine wave UPS. It's possible that the transformer for the router decided to turn off for some reason because of that (overheated, inadeuqate power, hard to say).
6) AFAIK that UPS doesn't have any kind of power saving sensing. Either it's on or it is off.
 
Joined
Sep 3, 2017
Messages
239 (0.10/day)
Location
Russia
Processor FX 8320 @4.2 | i7 2600 @3.8 | Xeon W3670 @ 3.6
Motherboard Asus Sabertooth R2.0 | Asus P8Z77-V Deluxe | Gigabyte X58-UD7
Cooling Zalman Performa 10+ | Zalman Performa 11+ | Zalman Performa 10+
Memory Crucial Ballistix Sport XT 32GB @ 1866 | Corsair Vengeance 32GB @1866 | Samsung 24GB @ 1600
Video Card(s) XFX Radeon 390x | Zotac GTX 1070 AMP Extreme | Zotac GTX 980 AMP Extreme
Storage Intel SSD / SAS 15k Fujitsu | Intel SSD / Velociraptors / Hitachi 2TB | Intel SSD / Samsung 1TB
Display(s) Samsung 245T | HP ZR30w | IBM 20" 4x3
Case Chieftec | Corsair Graphite 600T | Thermaltake Xaser IV
Audio Device(s) SB Titanium HD | SB Titanium HD | SB X-fi Elite Pro
Power Supply Thermaltake 875W | Corsair 850W | Thermaltake 1500W
Mouse Logitech | Logitech | Logitech
Keyboard Mitsumi Classic | Microsoft |Microsoft
Software W7 x64 | W7 x64 |W7 x64 / XP x32
Just replace batteries, they already damaged.
 

FordGT90Concept

"I go fast!1!11!1!"
Joined
Oct 13, 2008
Messages
26,259 (4.65/day)
Location
IA, USA
System Name BY-2021
Processor AMD Ryzen 7 5800X (65w eco profile)
Motherboard MSI B550 Gaming Plus
Cooling Scythe Mugen (rev 5)
Memory 2 x Kingston HyperX DDR4-3200 32 GiB
Video Card(s) AMD Radeon RX 7900 XT
Storage Samsung 980 Pro, Seagate Exos X20 TB 7200 RPM
Display(s) Nixeus NX-EDG274K (3840x2160@144 DP) + Samsung SyncMaster 906BW (1440x900@60 HDMI-DVI)
Case Coolermaster HAF 932 w/ USB 3.0 5.25" bay + USB 3.2 (A+C) 3.5" bay
Audio Device(s) Realtek ALC1150, Micca OriGen+
Power Supply Enermax Platimax 850w
Mouse Nixeus REVEL-X
Keyboard Tesoro Excalibur
Software Windows 10 Home 64-bit
Benchmark Scores Faster than the tortoise; slower than the hare.
Could be a manufacturing defect with the batteries, yeah. Usually if it is a dead cell, it's pretty consistent when it goes off relative to estimated time remaining. PowerPanel has a battery self test option if you haven't tried that yet.
 
Joined
Jul 25, 2006
Messages
12,014 (1.86/day)
Location
Nebraska, USA
System Name Brightworks Systems BWS-6 E-IV
Processor Intel Core i5-6600 @ 3.9GHz
Motherboard Gigabyte GA-Z170-HD3 Rev 1.0
Cooling Quality case, 2 x Fractal Design 140mm fans, stock CPU HSF
Memory 32GB (4 x 8GB) DDR4 3000 Corsair Vengeance
Video Card(s) EVGA GEForce GTX 1050Ti 4Gb GDDR5
Storage Samsung 850 Pro 256GB SSD, Samsung 860 Evo 500GB SSD
Display(s) Samsung S24E650BW LED x 2
Case Fractal Design Define R4
Power Supply EVGA Supernova 550W G2 Gold
Mouse Logitech M190
Keyboard Microsoft Wireless Comfort 5050
Software W10 Pro 64-bit
First, kudos for using a decent UPS. I wish every user would use them.

How old is this UPS - or rather, how old are the batteries? They generally have to be replaced every 3 - 5 years. Some times, they will last longer if not heavily used frequently.

Also, get a AC Outlet Tester to ensure your outlet is properly wired and grounded. I recommend one with a GFCI (ground fault circuit interrupt) indicator as it can be used to test bathroom and kitchen outlets (outlets near water) too. These testers can be found for your type and voltage outlet, foreign or domestic, (like this one for the UK) at most home improvement stores, or even the electrical department at Wal-Mart. Use it to test all the outlets in the home and if a fault is shown, have it fixed by a qualified electrician.

Many UPS will shutdown if not properly grounded.

Also, if there is a fault in the connected components, (the PC's PSU, for example) any good UPS will shut down to protect itself, and the other connected devices.

FTR, I never, as in NEVER EVER buy replacement batteries from the UPS maker. They always cost way too much. I always shop around and buy my UPS batteries from Apex, BatteryWholesale, Battery Mart, or Batteryplex, or Amazon depending on who has the best price at the time (factoring in shipping, which can be significant, but sometimes free).

For example, the 6 year old ( :)) old batteries I had in my APC SmartUPS I got last time from Battery Mart finally died a few weeks ago. APC wanted over $100 for the replacement cells, plus $20 for shipping. But as seen here, I was able to get 4 new cells for less than half of that. In many cases, I have peeled off the APC, Cyberpower, or Tripplite lables on the original batteries to see they are the exact same batteries as found at these outlets. APC, Cyberpower, Tripplite are UPS makers, not battery makers.

I have never been disappointed using 3rd party SLA batteries in the 25+ years I have used UPSs.
 
Joined
May 13, 2010
Messages
5,632 (1.11/day)
System Name RemixedBeast-NX
Processor Intel Xeon E5-2690 @ 2.9Ghz (8C/16T)
Motherboard Dell Inc. 08HPGT (CPU 1)
Cooling Dell Standard
Memory 24GB ECC
Video Card(s) Gigabyte Nvidia RTX2060 6GB
Storage 2TB Samsung 860 EVO SSD//2TB WD Black HDD
Display(s) Samsung SyncMaster P2350 23in @ 1920x1080 + Dell E2013H 20 in @1600x900
Case Dell Precision T3600 Chassis
Audio Device(s) Beyerdynamic DT770 Pro 80 // Fiio E7 Amp/DAC
Power Supply 630w Dell T3600 PSU
Mouse Logitech G700s/G502
Keyboard Logitech K740
Software Linux Mint 20
Benchmark Scores Network: APs: Cisco Meraki MR32, Ubiquiti Unifi AP-AC-LR and Lite Router/Sw:Meraki MX64 MS220-8P
You might need to do the following:

1)unplug everything from the UPS and unplug the UPS
2)removing the battery
3)hold down the power button for 30 seconds.
4)re-insert the battery
5)power the UPS on with it unplugged from the wall, pay attention to the beep codes and check what they mean
6)if it's all good then plug everything back in.
 

pubudeux

New Member
Joined
Oct 28, 2020
Messages
3 (0.00/day)
Hey, I registered to reply here as I found this page after searching "CyberPower UPS turning off randomly" looking for an answer. Through a mix of advice, I think I've found it - so it might be nice to help people in the future who find themselves in the same position.

As the original poster, I also had the UPS connected through usb to a server running PowerPanel software for Linux. One of the configuration options on the pwrstatd service is "turn-ups-off," which is only editable directly on /etc/pwrstatd.conf and not through the command line tool. Since it is enabled by default, when there is a power event the UPS will automatically shutdown after the default threshold (10 minutes).

For example, with the default config when I installed the pwrstatd software, if there is a power failure:

1) Elapsed time: 0 seconds - pwrstatd waits 60 seconds to run the "Action for Power Failure" command
2) Elapsed time: 60 seconds - It gives a grace period for running the command (default 0 sec)
3) Elapsed time: 60 seconds - It will schedule a UPS shutdown in the amount of time set in "shutdown-sustain" (default 600s)
4) Elapsed time: 60 seconds - It will shutdown the machine running the pwrstatd software
5) Elapsed time: 11 minutes - UPS will shutdown

So in this case, even if your UPS is mostly charged after 11 mins, with the default config it would power down all.
 
Joined
Jul 25, 2006
Messages
12,014 (1.86/day)
Location
Nebraska, USA
System Name Brightworks Systems BWS-6 E-IV
Processor Intel Core i5-6600 @ 3.9GHz
Motherboard Gigabyte GA-Z170-HD3 Rev 1.0
Cooling Quality case, 2 x Fractal Design 140mm fans, stock CPU HSF
Memory 32GB (4 x 8GB) DDR4 3000 Corsair Vengeance
Video Card(s) EVGA GEForce GTX 1050Ti 4Gb GDDR5
Storage Samsung 850 Pro 256GB SSD, Samsung 860 Evo 500GB SSD
Display(s) Samsung S24E650BW LED x 2
Case Fractal Design Define R4
Power Supply EVGA Supernova 550W G2 Gold
Mouse Logitech M190
Keyboard Microsoft Wireless Comfort 5050
Software W10 Pro 64-bit
So in this case, even if your UPS is mostly charged after 11 mins, with the default config it would power down all.
Which actually makes sense for several reasons with most scenarios.

The key and consistent unknown in this scenario is we don't know how long the power outage will last. It could be a couple more minutes, or days.

Most rechargeable battery technologies don't like the batteries to sit unused (or stored on the shelf) in a fully charged state for long periods of time. But it typically is worse for those rechargeable batteries to sit unused for long periods fully discharged. So after 10 - 11 minutes, they would be slightly discharged - a good thing.

At the same time, and most importantly, by shutting the UPS off after 11 minutes, there will still be enough charge remaining to support a "graceful" shutdown of the computer should there be a second power failure immediately after power is restored from the initial power outage.

In other words, this avoids the scenario where an extended power outage drains the batteries, power is restored and the computer boots up and then a minute later, the power fails again. Only this time, because the batteries are still drained, there is not enough battery runtime for the UPS monitoring program to save the open files, exit running programs and the OS, and "gracefully" shut down the computer properly. The computer simply crashes - never good.
 

pubudeux

New Member
Joined
Oct 28, 2020
Messages
3 (0.00/day)
I agree with your points, Bill. I just think it seems to be a point of confusion with users, as I saw many reviews on Amazon and posts talking about it turning off with full power when connected to USB management software.

I just think the manual of the pwrstat command should indicate that there are more additional parameters that handle power of the UPS itself in the conf file.
 
Joined
Jul 25, 2006
Messages
12,014 (1.86/day)
Location
Nebraska, USA
System Name Brightworks Systems BWS-6 E-IV
Processor Intel Core i5-6600 @ 3.9GHz
Motherboard Gigabyte GA-Z170-HD3 Rev 1.0
Cooling Quality case, 2 x Fractal Design 140mm fans, stock CPU HSF
Memory 32GB (4 x 8GB) DDR4 3000 Corsair Vengeance
Video Card(s) EVGA GEForce GTX 1050Ti 4Gb GDDR5
Storage Samsung 850 Pro 256GB SSD, Samsung 860 Evo 500GB SSD
Display(s) Samsung S24E650BW LED x 2
Case Fractal Design Define R4
Power Supply EVGA Supernova 550W G2 Gold
Mouse Logitech M190
Keyboard Microsoft Wireless Comfort 5050
Software W10 Pro 64-bit
Perhaps but then pwrstat is not Cyberpower's software. That is a 3rd party alternative. The official Cyberpower software is PowerPanel and that is the program the OP said he is using.

So two points here. (1) powerstat is not applicable to this thread and (2) if users are going to use 3rd party alternatives, the onus is on them to understand the program and on the 3rd party app developers to provide adequate documentatoin.
 

pubudeux

New Member
Joined
Oct 28, 2020
Messages
3 (0.00/day)
Just to clarify, the linux version of PowerPanel, when installed, the command is called pwrstat and the daemon is called pwrstatd.

 
Joined
Jul 25, 2006
Messages
12,014 (1.86/day)
Location
Nebraska, USA
System Name Brightworks Systems BWS-6 E-IV
Processor Intel Core i5-6600 @ 3.9GHz
Motherboard Gigabyte GA-Z170-HD3 Rev 1.0
Cooling Quality case, 2 x Fractal Design 140mm fans, stock CPU HSF
Memory 32GB (4 x 8GB) DDR4 3000 Corsair Vengeance
Video Card(s) EVGA GEForce GTX 1050Ti 4Gb GDDR5
Storage Samsung 850 Pro 256GB SSD, Samsung 860 Evo 500GB SSD
Display(s) Samsung S24E650BW LED x 2
Case Fractal Design Define R4
Power Supply EVGA Supernova 550W G2 Gold
Mouse Logitech M190
Keyboard Microsoft Wireless Comfort 5050
Software W10 Pro 64-bit
Okay. Thanks for that. However, not sure it applies here as this thread is 2 years old, there is no indication the OP was running Linux and the OP registered on the day he made that one and only post, then never returned.

IMO, your desire to help would have better served the site had you started a new thread with your information instead of dredging up this long-dormant thread. I'm just saying.
 